I did not accept several power panels (ranging from 40A to 300A) that a contractor installed on a new building - these panels haven't been detailed well enough on the system's design.
The reason I: instead of using bus bars rated the size of the main breaker for the panel, they used a mix of bars and jumper cables. The problem was that most the jumper cables were sized by the downstream circuit breaker that this jumper was feeding.
Example: 70A 3 pole breaker had a piece(+/-4 inches) of 100A bus bar and from this bar several jumper cables feeding individual breakers. If one of these jumpers would feed a 20A breaker, then the jumper would be only a 12 AWG. As this jumper was connected to a 70A breaker, I made him upgrade the jumper to at least a 4 AWG cable. The same happened in larger panels, like a 225A main that had 6 AWG jumpers connecting the 50A breaker, etc.
I made them replace all the jumpers with proper bus bars as much as possible, but given the lay out of the panel and also the fact that I had to deliver the building in a very short time, where bus bars wouldn't be possible to be installed I allowed them to use jumpers but they had to match the size of the breaker upstream from it.
The contractor did it, but now he is questioning my action. He is saying that the downstream breakers would limit the current on the jumpers and that what I made them remove was no code violation at all! He can be right, but how about the possibility of a short on the jumper wires between the main breaker and the one downstream???
Could you guys judge my action and let me know if this is or is not a NEC violation?
The reason I: instead of using bus bars rated the size of the main breaker for the panel, they used a mix of bars and jumper cables. The problem was that most the jumper cables were sized by the downstream circuit breaker that this jumper was feeding.
Example: 70A 3 pole breaker had a piece(+/-4 inches) of 100A bus bar and from this bar several jumper cables feeding individual breakers. If one of these jumpers would feed a 20A breaker, then the jumper would be only a 12 AWG. As this jumper was connected to a 70A breaker, I made him upgrade the jumper to at least a 4 AWG cable. The same happened in larger panels, like a 225A main that had 6 AWG jumpers connecting the 50A breaker, etc.
I made them replace all the jumpers with proper bus bars as much as possible, but given the lay out of the panel and also the fact that I had to deliver the building in a very short time, where bus bars wouldn't be possible to be installed I allowed them to use jumpers but they had to match the size of the breaker upstream from it.
The contractor did it, but now he is questioning my action. He is saying that the downstream breakers would limit the current on the jumpers and that what I made them remove was no code violation at all! He can be right, but how about the possibility of a short on the jumper wires between the main breaker and the one downstream???
Could you guys judge my action and let me know if this is or is not a NEC violation?