Sizing Conductors for a Transfer Switch

Status
Not open for further replies.

Little Bill

Moderator
Staff member
Location
Tennessee NEC:2017
Occupation
Semi-Retired Electrician
Let's say you have a 200A service and are using 2/0 cu conductors. You have a 200A service rated transfer switch. You run the 2/0 from the meter to the TS, and 2/0 to the panel from the TS. Now the generator is only around 80A. Do you have to run the same size (2/0) conductors from the generator to the TS? Or do you size them for the 80A?
 
Although if the generator had 200 amp breaker, you should be able to use 2/0 if it is only supplying the dwelling.
 
If the transfer switch is automatic, the generator must be sized to serve the total connected load or have load shedding devices to limit the load to the output of the generator.
 