The scenario is as follows:
1. 250at/af 75C main breaker w/ 250kcmil 75C 3phase/4wire cu feeder serving MCC to 250at/225af 75C breaker
2. Tap for lighting panel on load side of 250at/225af breaker
3. Panel board 240/120 100amp 1phase/ 3wire w/100amp 75C main breaker
4. Total LP load 2954 VA
5. Line current 13A/ea phase
Questions:
1. What codes apply for sizing conductors for a branch LP?
2. How would one determine the proper sizing of feeder conductors for this LP?
3. Are there any special considerations for the terminal connectors at the breakers?