Lightninarrester
Member
Guys, 1500KVA, 13.8kv delta - 480Y/277V Transformer. Primary OCPD is sized for 600% of 62.7A, use next Breaker rating 1200A. Secondary OCPD 125% of 1804A, 2255A, use next size 2500A Breaker. Question, do you size your conductors to the load or to your OCPD? , i.e. on secondary , you size them for 1804 plus 125% or to the rating of the secondary Breaker 2500A?