jatrottpe said:The 800% value for Instantaneouse circuit breaker typically refers to an adjustable circuit breaker (Motor Circuit Protector) (ie have a 50A breaker with an instantaneous adjustment of 300% - 1000% or so to allow for inrush current LRA). For the purposes of your problem, I believe you would be better off with the Inverse time breaker of 250% (250% x 28A = 70A breaker). Or a 50A breaker with an instantaneous trip setting of 400%; 400%x50=200A. assuming non energy effecient motor or 600% if motor is energy efficient)
Motor thermal protection - Looks good
Non-Fused Disconnect switch 35A is minimum, the industry standard sizes are 30A, 60A, 100A
The fuse size you referenced is correct, just make sure you show everything on your drawing (breaker at panel, fuse at motor, The inverse time breaker will cover the overcurrent and ground fault, the instantaneous breaker will require a fuse for short circuit).
These are things I don't know and has not been covered in my studies. I am pulling numbers out of the NEC. I looked at my numbers and thought any fuse or breaker set less than @168A will blow on start-up. I do realize the start-up Amps are only for less than a second, but haven't been taught the limits. I do know I can not run my coffee pot, microwave, and toaster at the same time on a 15A breaker, it tripps. Yes, I know I need to run a new line to the microwave, I change out the vent hood with a microwave. You know, wire was allready there.