Sizing direct buried USE cable

Status
Not open for further replies.

Rich Elec.

Senior Member
Location
Pennsylvania
Is table 310.16 the correct table for three direct buried USE cables.
These would be 120 volts.
I looked through the tables after 310.16 and none seem to apply.
I think that I am in the right place.

Thanks,
Rich
 
338.10 b 4 -> 334.80 (310.15 is mentioned, correction for bundling applies, I think table 310.16 would be the right one unless this is a dwelling service)
 
Last edited:
Is table 310.16 the correct table for three direct buried USE cables.
These would be 120 volts.
I looked through the tables after 310.16 and none seem to apply.
I think that I am in the right place.

Thanks,
Rich
That is the right table
Most people dont use that for 120 volt because it is usually only stocked in #2 100amp or larger . What will you be running it to .
 