Informal poll: When sizing a double neutral, do YOU size the neutral based on twice the overcurrent protection, or on twice the phase wire ampacity?
For example, with a 100A panelboard feeder using 2AWG phase wires, do you use a 3/0AWG neutral (2x100A=200A @75deg) or do you use a 4/0AWG (2x115A=230A wire ampacity)?
From what I have read, either will be sufficient. Just curious...