This is just a recount of a discussion - hoping to elicit comments. Hopefully non-trolling in nature. Questions are posed just as a starting place.
Talking with the crew yesterday on sizing an EBC. Here is the test case:
Motor: 50hp, normal stuff, not energy efficient - say Design B, Code G, 3ph, 460V, Nameplate current 62A, sf 1.15
Feeder is xhhw in RSC, specs say "green wire ground".
Conductors are 65A x 1.25 = 81.25A ==> #4CU (85A) (T430.250)
Overload set to 140% nameplate 62 x 1.40 = 86.8A
Branch Ckt OCP (430.52)
Select EBC (250.122.D)
We normally use an Instantaneous, so, size per 250.122.D.2 - max time delay fuse per 430.52.C.1, ex. 1
Supposing we used a TM CB, 175A EBC ==> #6Cu
Supposing we used a TM CB, 250A EBC ==> #4Cu
So:
Electricians:
Inspectors:
Design Engineers:
Field Dogs (engineers): I already know what you will do. Still, comments welcome
ice
Talking with the crew yesterday on sizing an EBC. Here is the test case:
Motor: 50hp, normal stuff, not energy efficient - say Design B, Code G, 3ph, 460V, Nameplate current 62A, sf 1.15
Feeder is xhhw in RSC, specs say "green wire ground".
Conductors are 65A x 1.25 = 81.25A ==> #4CU (85A) (T430.250)
Overload set to 140% nameplate 62 x 1.40 = 86.8A
Branch Ckt OCP (430.52)
Instantaneous 1300% 65 x 13 = 845A Not to exceed ==> 800A
Thermal-Mag 250% 65X 2.5 = 162.5A Next size ==> 175A
Thermal-Mag 400% 65 x 4.0 = 260A Not to exceed ==> 250A
Thermal-Mag 250% 65X 2.5 = 162.5A Next size ==> 175A
Thermal-Mag 400% 65 x 4.0 = 260A Not to exceed ==> 250A
Select EBC (250.122.D)
We normally use an Instantaneous, so, size per 250.122.D.2 - max time delay fuse per 430.52.C.1, ex. 1
65 x 1.75 = 113.75A next size up ==> 125A
per T250.122 ==> #6CU
Interesting Note: Under 2005, 250.122.D, the EBC was sized by the overload, and would have been a #8Cu
per T250.122 ==> #6CU
Interesting Note: Under 2005, 250.122.D, the EBC was sized by the overload, and would have been a #8Cu
Supposing we used a TM CB, 175A EBC ==> #6Cu
Supposing we used a TM CB, 250A EBC ==> #4Cu
So:
Electricians:
Field installed, no prints - Is this what you guys (and girls) are doing (seeing)?
Installed per prints - Are you seeing EBC sizes in this range? Smaller? Bigger?
Installed per prints - Are you seeing EBC sizes in this range? Smaller? Bigger?
Inspectors:
How are you looking at this? Is this anything you ever check?
Design Engineers:
How are you guys (and girls) doing this? If you use TM CBs do you account for possibly needing to change out CB for a 400%?
Field Dogs (engineers): I already know what you will do. Still, comments welcome
ice