If the building has one standby generator/ATS to back up the whole building load (or main service panel load),
can the standby generator be sized less than normal service panel size? i.e. We had a project, we calculated total
total building load is around 400kW. We planned to size the standby gen. set at 400kW load as well as the building has only one
ATS.
The client said based on historical data from similar building they want 200kW generator instead, the ATS is still sized
to support 400kW load, will this 200kW generator be code compliant? Thanks.