Hello,
I built a sub panel that is 200 amps 3 phase. I used 4/0 to feed the load carrying conductors and went with a 6 AWG off of table 250.122 for my equipment grounding conductor and failed my inspection. I was told that 250.122 (B) says that my equipment grounding conductor “shall be increased in size proportionately according to the circular mil area of the ungrounded conductors. I did increase my ungrounded conductors from 3/0 to 4/0. I thought I would be ok because in Table 250.122 it says it goes up to anything below 300 amps over current device. What do you think?
I built a sub panel that is 200 amps 3 phase. I used 4/0 to feed the load carrying conductors and went with a 6 AWG off of table 250.122 for my equipment grounding conductor and failed my inspection. I was told that 250.122 (B) says that my equipment grounding conductor “shall be increased in size proportionately according to the circular mil area of the ungrounded conductors. I did increase my ungrounded conductors from 3/0 to 4/0. I thought I would be ok because in Table 250.122 it says it goes up to anything below 300 amps over current device. What do you think?