I have a 600A overcurrent device on a long feeder run. Per 250.0122 it would require a #1cu ground before any adjustment for voltage drop. I am running 3 sets of 350kcmill to accomidate for voltage drop. When I calculate what the revised ground should be using the example from the handbook 250.122, B the answer does not seen correct to me.
Example 1
600A conductor per 310.16 = 1500 kcmill
3*350kcmill conductors = 1050 kcmill
1050/1500 = .7
I take this to mean that even tho I up sized the current carring conductiors the ground does not need to upsized?
Example 2
But if you use 2 set of 350's as your starting point the calculation becomes
1050/700= 1.5 which directs you to a 2/0 ground
Example 3
Or if you use 4 sets of 1/0 you get
1050000/422400 = 2.4 which directs you to a 4/0 ground
Can this be correct that by the tables in the code (using 1500kcmill) the ground does not need to be upsized in this case?
And what about is changing depending on how you parallel it?