If you size a motor branch circuit ocp per code. Does the equipment grounding conductor have to be size to the overcurrent device in this situation or just to the Full load current . What I have is:
20hp motor at 54A x 250% = 135A up it to 150A
Conductor 54A x 125% = 67.5A or a #4 Thhn conductor for phase conductors
What size would the grounding conductor have to be per code.