I have a job a could use a little advice/reassurance on. It is a commercial space, a granite company. They are installing a new piece of equipment for cutting granite. The only electrical information provided by the manufacturer of this equipment is the following:
There are 2 required power hookups to the TITAN with
the requirements as listed below:
NOTE: Power run must be completed by a licensed electrician.
TITAN Electric Requirements
480 VAC (+/-10%), 3 phase, 60 Hz, 30.0 Full Load Amps
(A 60 amp thermal-magnetic main breaker is factory installed inside the electrical enclosure)
OH Laser Electric Requirements
Standard 120 VAC 15 amp electrical outlet
(Outlet MUST be within 25’ of the laser post location, refer to the installation
drawing for details)
Sizing equipment like this needless to say is not my bread and butter. However, from what I remember and what I have looked up. The equipment is not to be sized off of the nameplate rating but rather the HP/FLC using table 430.250. I would multiply the FLC by 125% which would give me my wire size. Then use the FLC found on table 430.250 and reference table 430.52 to get my breaker size. Table 250.122 for equipment grounding conductor size.
Am I right to say I need more info? Like the HP of the motor, motor type?
When should a fused disconnect be used over a non fused disconnect for something like this?
Any help would be much appreciated.
There are 2 required power hookups to the TITAN with
the requirements as listed below:
NOTE: Power run must be completed by a licensed electrician.
TITAN Electric Requirements
480 VAC (+/-10%), 3 phase, 60 Hz, 30.0 Full Load Amps
(A 60 amp thermal-magnetic main breaker is factory installed inside the electrical enclosure)
OH Laser Electric Requirements
Standard 120 VAC 15 amp electrical outlet
(Outlet MUST be within 25’ of the laser post location, refer to the installation
drawing for details)
Sizing equipment like this needless to say is not my bread and butter. However, from what I remember and what I have looked up. The equipment is not to be sized off of the nameplate rating but rather the HP/FLC using table 430.250. I would multiply the FLC by 125% which would give me my wire size. Then use the FLC found on table 430.250 and reference table 430.52 to get my breaker size. Table 250.122 for equipment grounding conductor size.
Am I right to say I need more info? Like the HP of the motor, motor type?
When should a fused disconnect be used over a non fused disconnect for something like this?
Any help would be much appreciated.