jtgrace87
Member
- Location
- Bowling Green, KY, USA
I am trying to size a feeder breaker that will feed (3) 25HP, 35 FLA motors. Each motor will be controlled by a drive. One of the motors and drives will not be used and will be installed as an online spare incase of a breakdown. Each drive contains a 50A Circuit Breaker on the Line Side, so one of these will be open and locked until needed. So for sizing this feeder breaker, should I size it using only two motors since they will be the only two pulling load on the circuit or should I size using all three motors?
I will be using NEC 430.24 to size my feeder breaker:
Option 1- Two Motors
(35*1.25)+35= 78.75A (use an 80A Feeder Breaker)
Option 2- Three Motors
(35*1.25)+35+35= 113.75 (Use a 125A Feeder Breaker)
I will be using NEC 430.24 to size my feeder breaker:
Option 1- Two Motors
(35*1.25)+35= 78.75A (use an 80A Feeder Breaker)
Option 2- Three Motors
(35*1.25)+35+35= 113.75 (Use a 125A Feeder Breaker)