Sizing Feeder coming off a bus plug.
Bwear
Wisconsin
Electrician Apprentice
I am an apprentice and wanting to better understand how sizing a feeder from a bus plug works. Say I have an equipment power panel with a 30A Main Circuit Breaker. Assuming continuous duty, do I multiply the 30A x 125%. Which comes out to 37.5A Would you fuse the Bus Plug at 40A and pull #8 THHN to it?
Yes your calculation (30*125%) is correct for a continuous load. Not sure what you mean by a bus plug, do you mean a circuit beaker?