I'm thinking about incorporating subpanels into our building design and was looking for a double-check on my calculations.
I need to size the feeder to a 400 amp subpanel. We are distributing power at 3 phase 415 wye. The subpanel has six 60A three phase circuits on it. Each circuit will be used continuously at 80% for a total continuous load of 288 A.
What gauge wire do I need, if I'm using aluminum? Can I use more than one conductor per phase for the feeder? What number of conductors is optimal to achieve the greatest amps to cross-sectional area ratio?
Thanks!