Sizing feeder for a chiller

Status
Not open for further replies.

Zapp20

Member
Location
CT
I have a 1200 ton Chiller, MCA is 1192 amps at 480 volts with a MOP of 2000 amps at Name Plate. I looked at the Table under 75'C i'm thinking 4 sets of 350 MCM should do it. Am I correct? I'm in CT which adopted the 2014 NEC.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
If your MCA is 1192A, your conductors total ampacity needs only to be sufficient for that, not the 2000A MOCP.

3 sets of 250 kcmil CU would work. 3 x 405A = 1215A


I think that you got the wrong table 250 kcmil is only good for 255 amps/set.

4 sets of 350's will work 300*4=1200
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I have a 1200 ton Chiller, MCA is 1192 amps at 480 volts with a MOP of 2000 amps at Name Plate. I looked at the Table under 75'C i'm thinking 4 sets of 350 MCM should do it. Am I correct? I'm in CT which adopted the 2014 NEC.


Yes that should work assuming there is no derating
 