Thanks for taking the time to read this. I am stumped on this and may be obvious to others on this forum. I do not conduct a lot of load calculations and a little rusty. My math is not the best as well. If I am missing something from my calculations, please let me know. I checked sections 220, 430, and Annex D and I am still kind of lost.
I am installing a Square D, 3 phase S/P fed by a 240/120 volt 3 phase Delta service. This is a commercial laundry shop so my understanding is that everything is calculated at 100% demand. The new circuitry added is as follows:
1. Two 3 phase, 240 volt commercial washers with FLA of 22.5 amps. The minimum size CB per specs is 40 amp per unit on these units. My calculation for this is: 22.5 amps x 240 x 1.73 = 9,342 VA; There are total of two washers connected to this S/P, so total VA on this will be 18,684.
2. One single phase, residential dryer (not sure why he wants a residential dryer). This is 5,000 VA I believe. (Also I realize this must be wired to A and C phase, as the motor is 120 volts to ground).
3. One 3 phase, 240 volt gas dryer. FLA 6 amps x 240 x 1.73 = 2,491 VA.
Total VA among the 4 appliances is 26,175 VA/240 = 109 amps. So feeder protected by 110 amp 3 pole CB?
These are non-continous loads so I don't need to multiply by 1.25. I feel that I am missing something and if someone could guide me to the right code section, it would be greatly appreciated.
Thank you and Happy Easter!
I am installing a Square D, 3 phase S/P fed by a 240/120 volt 3 phase Delta service. This is a commercial laundry shop so my understanding is that everything is calculated at 100% demand. The new circuitry added is as follows:
1. Two 3 phase, 240 volt commercial washers with FLA of 22.5 amps. The minimum size CB per specs is 40 amp per unit on these units. My calculation for this is: 22.5 amps x 240 x 1.73 = 9,342 VA; There are total of two washers connected to this S/P, so total VA on this will be 18,684.
2. One single phase, residential dryer (not sure why he wants a residential dryer). This is 5,000 VA I believe. (Also I realize this must be wired to A and C phase, as the motor is 120 volts to ground).
3. One 3 phase, 240 volt gas dryer. FLA 6 amps x 240 x 1.73 = 2,491 VA.
Total VA among the 4 appliances is 26,175 VA/240 = 109 amps. So feeder protected by 110 amp 3 pole CB?
These are non-continous loads so I don't need to multiply by 1.25. I feel that I am missing something and if someone could guide me to the right code section, it would be greatly appreciated.
Thank you and Happy Easter!