I understand the code associated with sizing feeders for multiple motor loads and feeds to industrial control panels (430.62 and 409.21), but what if we wanted to oversize those feeders for future loads? We can't per code, because we are limited to 125% of the largest motor OCP size plus all other connected loads (plus 125% of any continuous loads that might be connected to the feeder). How far do we take this?
Case in point, if an industrial control panel is serving several motors, each with its own properly sized branch circuit over-current protection and properly sized distribution within the control panel, then why can't the feeder to the industrial control panel be upsized based on a possible future load?
Am I missing something here?
Case in point, if an industrial control panel is serving several motors, each with its own properly sized branch circuit over-current protection and properly sized distribution within the control panel, then why can't the feeder to the industrial control panel be upsized based on a possible future load?
Am I missing something here?