Sizing feeders going to two x-formers

Merry Christmas
Status
Not open for further replies.

Sharpie

Senior Member
Location
PA
I have a set of feeders (1 AWG, 3ph, 480V.) Traveling 540 ft. one direction. These feed a 480/208, 75 KVA X-former (lightly loaded though). The customer wants me to tap off the same 480V circuit at the end of the run, go into a breaker or fused disconnect, and run 2 AWG, 1ph 480V an additional 500 ft. to a 480/240 x-former for a 150A 240V panel.

I have been searching through art. 215, 220, and 225 to see if this application is acceptable. All I'm seeing though is that you have to do a load calc. on the existing before adding to it.

I'm wondering if I should down-size the transformers to more closely represent the load that is there.

Any thoughts?

Thanks
 
Without taking into account voltage drop or "inrush" problems, if your transformers meet 450.3 as far as primary and secondary overcurrent protection I don't see any NEC problems offhand.
It doesn't appear to be such a great idea, but I beleive it's code compliant.
 
Thanks Augie.

That's where I'm at. I don't think it's a code violation, but I do think it sets the stage for future problems.
 