I was discussing with my apprentice the size of conductors required to supply power for a 200 amp., residential service.
I told him we are going to use 4/0 Al., per Table 310-15 (B) 7. Due to the fact that the sub panel is a good 10' away from the point of entry,
I'm going to install a 200 amp service disconnect at the point of entry. Then run 4/0 SER Al., to the sub panel. Grounding to h2o pipe with
#4 cu. and to ground rod with #6 cu. He thought we should use 250 kcmil. Comment?
I told him we are going to use 4/0 Al., per Table 310-15 (B) 7. Due to the fact that the sub panel is a good 10' away from the point of entry,
I'm going to install a 200 amp service disconnect at the point of entry. Then run 4/0 SER Al., to the sub panel. Grounding to h2o pipe with
#4 cu. and to ground rod with #6 cu. He thought we should use 250 kcmil. Comment?