Good Morning all - this may be a relatively easy question for most of you to answer, but I am kind of new to the forum, and still fairly green when it comes to 3 phase commercial equipment. My questions is...
I have a 250kw 3phase/4wire generator, 480/277v with two fused outputs. One breaker is a 200amp 3 pole, the other a 225amp 3pole. When sizing my feeders - I believe I am going to refer to table 310.16 as the norm, but being it is 3 phase, I feel I have to refer to 315.b where there are four-six current carrying conductors in a raceway derate 80%.
The reason why I am asking this is because a licensed electrician bid the project utilizing 2/0 copper for both sets of feeders. I believe this is incorrect and want to make sure we are covered.
I think I should be using 250MCM copper for the 200Amp transfer switch - which is 250MCM good for 255Amps at 80% is 204 amps.
I think I should be using 300MCM copper for the 225 transfer switch -
which is 300MCM good for 285 at 80% is 228 amps.
Can someone let me know if I am over engineering this? Are there special instances where I can utilize a smaller feeder such as 2/0? If so, where can I find this in the NEC? Or am I sizing my feeders correctly?
I thank you all in advance. And look forward to your responses. Enjoy the day!
I have a 250kw 3phase/4wire generator, 480/277v with two fused outputs. One breaker is a 200amp 3 pole, the other a 225amp 3pole. When sizing my feeders - I believe I am going to refer to table 310.16 as the norm, but being it is 3 phase, I feel I have to refer to 315.b where there are four-six current carrying conductors in a raceway derate 80%.
The reason why I am asking this is because a licensed electrician bid the project utilizing 2/0 copper for both sets of feeders. I believe this is incorrect and want to make sure we are covered.
I think I should be using 250MCM copper for the 200Amp transfer switch - which is 250MCM good for 255Amps at 80% is 204 amps.
I think I should be using 300MCM copper for the 225 transfer switch -
which is 300MCM good for 285 at 80% is 228 amps.
Can someone let me know if I am over engineering this? Are there special instances where I can utilize a smaller feeder such as 2/0? If so, where can I find this in the NEC? Or am I sizing my feeders correctly?
I thank you all in advance. And look forward to your responses. Enjoy the day!