MikeStewart
- Charleston, SC
- Manager
I am trying to size the conductors for a three phase 460v fire pump motor. The fire pump motors manufacturer didn’t list the amps required for the motor on the name plate but they did list the max brake horsepower as 207.
Looking at Table 430.250 it doesn’t have a horsepower rating of 207 so I have to round up to 250 hp, wow. So now the table states I need to figure the motor is running at 302 amps. So I take the 302 and multiply it by 1.25 (25%) and I have a total of 377.5 amps. I’m assuming now divide that by 3 to be 126 amps per phase before I utilize table 310.16 and 310.15(B)(1)(1) (it’s an unconditioned pump house in the south).
My question Is, is there a formula I can use so I don’t have to take such a large hit rounding up from 207 to 250 on the horsepower? Can I add the 25% before if not? And probably the easiest question, when do I calculate the resistance in my wire length?