I have a 20HP motor with a nameplate of 230V ,3phase, 47 amps. So to size the breaker feeding the motor, you use Table 430-250 for the amperage for 20hp, and mutiply times the values given in 430-52 (In this case we are using a breaker) of 250%. That would be 54A x 250% = 135A. So can I go down to a 125A breaker to feed this motor and be to code. Also the conductor size is based on 430-50 current values X 125% = 67.5a. So the conductor would need to be a #4. The motor is approx. 100' from the panel. So with all this said will this be code compliant for this motor installation.