I haven't posted in a while, but I'm back.
We have a small extruder from Europe that needs a three phase 400V, 50 hz with a 4 wire plus ground feed.
At our plant, we have three phase 480v, 60 HZ, 3 wire plus ground available.
The schematics don't show the breaker size, but it does show a main disconnect switch rated at 63 amps with a 6mm^2 wires (a hair bigger than 10 guage)
Its an older unit, does not show main breaker size unfortunately.
The extruder has a few motors that add up to 8 KVA (normal motors, no VFD's)
There is another 4 KVA in heaters.
So I looked online at ATO frequency converters and Advanced power and controls. If you have experience with either manufacturer, please let it be know.
At any rate, if you look at a typical motor chart, it says to roughly double the KVA of your motor total to size your transformer. (I know, there are many variations on this)
If this is the case, I need 8KVA x 2 = 16KVA. Add in my heaters and I need a transformer at 21 KVA .....or a 30 KVA would prob be a good guess.
When I talk to the manufacturer, they say this:
Ok, just note that we size the converter based on motor inrush current at starting period, Not rated current/power, and the motor inrush current/power is approx 6-7 times its rated current/power, so recommended frequency converter model: HZ-50-3360, 60kVA power capacity, input: 3ph, Delta (L1,L2,L3 + G), 480V (+/- 10%), 50/60Hz and output: 3ph, Wye/Delta (L1,L2,L3 + N,G), adjustable (0-520V), adjustable (40-120Hz), 83.2A.
So they literally took my 8 KVA and multiplied it by 7 to get 56KVA plus 4 KVA in heaters.
My question is, why the discrepancy between the manufacturer and the motor chart? Are they trying to up sell or is it legit?
I (we) need to UNDERSTAND why !!?? Perhaps they are being ultra conservative to avoid problems? Prob not a bad idea.
We have a small extruder from Europe that needs a three phase 400V, 50 hz with a 4 wire plus ground feed.
At our plant, we have three phase 480v, 60 HZ, 3 wire plus ground available.
The schematics don't show the breaker size, but it does show a main disconnect switch rated at 63 amps with a 6mm^2 wires (a hair bigger than 10 guage)
Its an older unit, does not show main breaker size unfortunately.
The extruder has a few motors that add up to 8 KVA (normal motors, no VFD's)
There is another 4 KVA in heaters.
So I looked online at ATO frequency converters and Advanced power and controls. If you have experience with either manufacturer, please let it be know.
At any rate, if you look at a typical motor chart, it says to roughly double the KVA of your motor total to size your transformer. (I know, there are many variations on this)
If this is the case, I need 8KVA x 2 = 16KVA. Add in my heaters and I need a transformer at 21 KVA .....or a 30 KVA would prob be a good guess.
When I talk to the manufacturer, they say this:
Ok, just note that we size the converter based on motor inrush current at starting period, Not rated current/power, and the motor inrush current/power is approx 6-7 times its rated current/power, so recommended frequency converter model: HZ-50-3360, 60kVA power capacity, input: 3ph, Delta (L1,L2,L3 + G), 480V (+/- 10%), 50/60Hz and output: 3ph, Wye/Delta (L1,L2,L3 + N,G), adjustable (0-520V), adjustable (40-120Hz), 83.2A.
So they literally took my 8 KVA and multiplied it by 7 to get 56KVA plus 4 KVA in heaters.
My question is, why the discrepancy between the manufacturer and the motor chart? Are they trying to up sell or is it legit?
I (we) need to UNDERSTAND why !!?? Perhaps they are being ultra conservative to avoid problems? Prob not a bad idea.