I'm helping with the installation of a new compressor. I want to check my calculations to ensure the correct disconnect and fuses are installed. The tech from the manufacturer told me to install number 10's and a 40 amp breaker. This seems incorrect to me so I'm already thinking of changing these conductors to number 8's especially since the breaker is over 100 feet from the disconnect. He also told me to install a 30 amp fusable disconnect. So the motor will be on 460 volts, 22 FLA, 15 hp. Does it sound correct to use 30 amp fuses for this motor at the disconnect?
my second question concerns a switch which is being used to alternate between two compressors currently in use. One compressor is being replaced with the new one I mentioned above and the other compressor will remain but won't be needed as often. They want to be able to use some kind of control to alternately switch between the two compressors. They each have different voltage and current ratings. Can anyone recommend where I would start to look for solutions? What kind of control device would I need and is it logical to use one?
thank you
my second question concerns a switch which is being used to alternate between two compressors currently in use. One compressor is being replaced with the new one I mentioned above and the other compressor will remain but won't be needed as often. They want to be able to use some kind of control to alternately switch between the two compressors. They each have different voltage and current ratings. Can anyone recommend where I would start to look for solutions? What kind of control device would I need and is it logical to use one?