sizing GEC for dual conductors

Status
Not open for further replies.

Steviechia2

Senior Member
Location
Massachusetts
I have 2 sets of 750 mcm conductors and am trying to figure my egc sizing. I'm on table 8 and I forgot which column I have to look at. I believe it's the stranding, diameter column? this would put me with a 3/0 copper conductor
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
In this case you don't need Table 8 as you have kcmil sizes already.
(2) 750 kcmil = 1,500 kcmil. From 250.66, that's over 1000 so it's a 3/0 cu or 250 al for your GEC.
Be cautious however, for a bonding jumper {250.24(B)}you need to keep the 12-1/2 % rule in mind
 
Last edited: