Hey all! First time posting as I've found tons of great information reading over the years. I have a question regarding the GEC for a 600A system for my building. Long story short, I needed to move my weatherheads to accommodate gutters, which involved POCO, which meant moving/relocating a CT cabinet, which turned into running all new wiring underground, new CT cabinet outside, adding a main disconnect (previously CT inside ran right into 600A MDP), Anyways, previous wiring was parallel 350mcm wire (560A capacity), so I'm running new Aluminum parallel 600mcm for cost and 616A capacity. Onto my actual question... I have confirmed with POCO that the CT cabinet gets its own ground rod, bonded to neutral and cabinet, and they run that ground into the new meter can.
From the CT cabinet, I have 4" PVC through two sets of Mogul LB's into my 600A fusible disco. Since the disconnect becomes my new service entrance, I know that neutral and ground gets bonded there and nowhere after that. Previously the only building's GEC was from the old CT to the water pipe. I have two 5/8" copper ground rods I was going to drive 6' apart either outside right on the other side of the wall or inside through the slab. I understand that wire doesn't need to be any bigger than 6AWG and some people typically just do 4AWG 7 strand bare. I also have the option to run to building steel (metal beams, metal deck roof, CMU walls) and home run up to the water supply pre or post meter. Per 250.66, the GEC to either of those would be 2/0 copper and land all back at the disco.
Does it make sense to do all three GEC to make for a good system? I don't have the option to do a Ufer. Second, if I do add the 2/0 to the steel and water pipe, does the wire to the ground rods have to be increased to 2/0 as well or does that stay 4 or 6AWG? I'll edit and attach a couple pics to help it make sense once I can.
Thanks in advance!
From the CT cabinet, I have 4" PVC through two sets of Mogul LB's into my 600A fusible disco. Since the disconnect becomes my new service entrance, I know that neutral and ground gets bonded there and nowhere after that. Previously the only building's GEC was from the old CT to the water pipe. I have two 5/8" copper ground rods I was going to drive 6' apart either outside right on the other side of the wall or inside through the slab. I understand that wire doesn't need to be any bigger than 6AWG and some people typically just do 4AWG 7 strand bare. I also have the option to run to building steel (metal beams, metal deck roof, CMU walls) and home run up to the water supply pre or post meter. Per 250.66, the GEC to either of those would be 2/0 copper and land all back at the disco.
Does it make sense to do all three GEC to make for a good system? I don't have the option to do a Ufer. Second, if I do add the 2/0 to the steel and water pipe, does the wire to the ground rods have to be increased to 2/0 as well or does that stay 4 or 6AWG? I'll edit and attach a couple pics to help it make sense once I can.
Thanks in advance!