johnson151
Member
- Location
- Idaho
- Occupation
- Electrician
I have a 100 amp service that will be fed from the power company with 1/0 AL. The grounding electrode is a rebar coming out of the concrete. I installed a #6 solid copper wire between the service panel and the rebar as the grounding electrode conductor. The inspector cited 250.66(B) and says that a #4 must be installed. The last sentence of this paragraph says "shall not be required be larger than #4awg" To me this says #4 is the maximum size I would need, and that I should size the GEC off of table 250.66 until conditions surpass what would otherwise call for larger that #4. The only evidence I can see that would support his argument is if that final statement means "is required to be #4".
He has asked a few other inspectors and they all say #4, but haven't been given a solid reference or piece of evidence to support it.
Can anyone else point me to what they may be referring too? Or, if I'm correct, is there a better reference or resource I can give to prove my case?
I found this video that seems pretty clear to me, but the only thing the inspector said was "is Mike Holt the AHJ?"
As for now, I'll just put in #4 from now on to avoid the fight, but I would like to know what the answer is.
Thanks in advance
He has asked a few other inspectors and they all say #4, but haven't been given a solid reference or piece of evidence to support it.
Can anyone else point me to what they may be referring too? Or, if I'm correct, is there a better reference or resource I can give to prove my case?
I found this video that seems pretty clear to me, but the only thing the inspector said was "is Mike Holt the AHJ?"
As for now, I'll just put in #4 from now on to avoid the fight, but I would like to know what the answer is.
Thanks in advance