zander
Member
Hello Everyone,
I'm installing a 320 amp service, 2x 200 amp breakers in the pedestal, 2x separate 4/0, 4/0, 4/0, 2/0 SER cables run to 2x separate 200 amp panels in the basement, 2x ground rods tied together with #4 bare (I know I could have gotten away with #6) run back to both panels.
Here is the question.
Table 250.66 says that the GEC is based on the size of the largest ungrounded conductor or equivalent area for PARALLEL CONUCTORS. Taking that word for word, I came to the conclusion that a #4 bare copper wire would meet those requirements. The inspector, however, is saying that the size of the GEC should be based on the 320 amp service rating. I don't agree with this because the 2x 200 amp feeds going to the panels are by definition individual, and not parallel. What is the general consensus on this? Thank you in advance.
I'm installing a 320 amp service, 2x 200 amp breakers in the pedestal, 2x separate 4/0, 4/0, 4/0, 2/0 SER cables run to 2x separate 200 amp panels in the basement, 2x ground rods tied together with #4 bare (I know I could have gotten away with #6) run back to both panels.
Here is the question.
Table 250.66 says that the GEC is based on the size of the largest ungrounded conductor or equivalent area for PARALLEL CONUCTORS. Taking that word for word, I came to the conclusion that a #4 bare copper wire would meet those requirements. The inspector, however, is saying that the size of the GEC should be based on the 320 amp service rating. I don't agree with this because the 2x 200 amp feeds going to the panels are by definition individual, and not parallel. What is the general consensus on this? Thank you in advance.