We have a customer that has an Emergency System, diesel generator, single ATS, one distribution panel. The Generator is Rated 30 KW 37.5 KVA @. 8pf 480/277 3-phase 4-wire wye 36.1 amps Full Load with a 50 amp main circuit breaker.
They recently added an additional emergency lighting, increasing the load from, 25/27/21 amps per phase to 30/31/29 amps per phase. An electrical contractor did a site review for the building and told the customer that he has violated the NEC and the NFPA 70. That the full load capacity of a diesel generator is limited to 80% of full load KW rating and their generator should be replaced ASAP.
I have worked around generators for years servicing, installing and load testing and while limiting load to 80% is a good practice I can not locate any reference in the NEC/NFPA 70 nor NFPA 110 regarding limiting the load to 80%…………Am I missing something?
They recently added an additional emergency lighting, increasing the load from, 25/27/21 amps per phase to 30/31/29 amps per phase. An electrical contractor did a site review for the building and told the customer that he has violated the NEC and the NFPA 70. That the full load capacity of a diesel generator is limited to 80% of full load KW rating and their generator should be replaced ASAP.