If using a 208/480V step up transformer, can you adjust the ground conductor based on what the secondary OCPD would have been? If not, you would have to size the ground conductor on the secondary based on the primary OCPD right?
For instance, a 1600A OCPD on the primary would require a #4/0 ground. For the secondary, a 600A OCPD would allow #1 ground (although secondary OCPD not allowed for fire pumps) but can you size the secondary ground conductor based on this 600A OCPD or do you have go off of the 1600A OCPD?
For instance, a 1600A OCPD on the primary would require a #4/0 ground. For the secondary, a 600A OCPD would allow #1 ground (although secondary OCPD not allowed for fire pumps) but can you size the secondary ground conductor based on this 600A OCPD or do you have go off of the 1600A OCPD?