I am doing a 200 amp sub feed in a residential home. Normally I would run aluminum SER cable which has three 4/O (2 hots, a neutral, and a 2/O ground). For this house I'm running PVC conduit with individual XHHW aluminum wire.
So my question is on the size of the ground. In the manufacturer's SER cable it's a 2/O, but according to the 2005 NEC chart 250.66, it says I need a 2 AWG, and if I use chart 250.122 it says I need a 4 AWG. So why does the SER cable have a 2/0 in it, which is by code much larger than what is needed?
So my question is on the size of the ground. In the manufacturer's SER cable it's a 2/O, but according to the 2005 NEC chart 250.66, it says I need a 2 AWG, and if I use chart 250.122 it says I need a 4 AWG. So why does the SER cable have a 2/0 in it, which is by code much larger than what is needed?