We are looking at replacing an existing 4000A service entrance switchboard and feeders and am trying to determine the best approach to sizing grounded conductor (neutral). I'm not sure if the existing facility has any 277 L-N loads which leaves me debating weather nor not I need to pull a full size neutral or just size the neutral per requirements of 230.24 (C).
If I have a situation where I don't have any L-N loads I know that 230.24(C) tells me that I can reference Table 250.102(C)(1) to determine size of grounded conductor which will be a smaller size than the phase conductors. However if I have L-N loads then I need to consider the grounded conductor as a neutral conductor carrying neutral current and need to size the neutral to carry unbalanced current. Without knowing the existing L-N loads that may exist (or may be added in future) do I need to consider this to be a full size neutral or is there a provision that allows me to used reduced neutral size (I know provision exists but cant put my finder on code section).
If the neutral is considered a current carrying conductor in a service do the requirements of Table 310.15(B)(3)(a) apply for adjusting cable ampacity for having 4 current carrying conductors in a raceway. Assuming the neutral is a CCC any applying adjustment factors we come up with 10 Sets of 4/C 750MCM for service entrance. Existing installation had 11 Sets of 4/C 500MCM which indicates that they pulled full neutral but did not de-rate for 4th CCC.
I was hoping to hear thoughts from others on approach here for replacement of service.
If I have a situation where I don't have any L-N loads I know that 230.24(C) tells me that I can reference Table 250.102(C)(1) to determine size of grounded conductor which will be a smaller size than the phase conductors. However if I have L-N loads then I need to consider the grounded conductor as a neutral conductor carrying neutral current and need to size the neutral to carry unbalanced current. Without knowing the existing L-N loads that may exist (or may be added in future) do I need to consider this to be a full size neutral or is there a provision that allows me to used reduced neutral size (I know provision exists but cant put my finder on code section).
If the neutral is considered a current carrying conductor in a service do the requirements of Table 310.15(B)(3)(a) apply for adjusting cable ampacity for having 4 current carrying conductors in a raceway. Assuming the neutral is a CCC any applying adjustment factors we come up with 10 Sets of 4/C 750MCM for service entrance. Existing installation had 11 Sets of 4/C 500MCM which indicates that they pulled full neutral but did not de-rate for 4th CCC.
I was hoping to hear thoughts from others on approach here for replacement of service.