Sizing grounded conductor? per Note 1 under Table 250.102(C)(1) with 12.5% rule

Status
Not open for further replies.

housemoney

Member
Location
Midwest
Occupation
Engr
If your total Equivalent area of Ungrounded parallel conductors is over 1100 kcmil copper or 1750 kcmil AL (example 4 parallel runs of 500s= 2000kcmils) are you *required* to use the 12.5% rule for Sizing your minimum grounded conductor and *not to* use table .102 c / 1 ?
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
See Note 3 to the Table. For the grounded service conductor it depends on there being in one raceway or multiple raceways.
If you have (4) 500s in (4) separate raceways, each would have a 1/0 unless larger is required by load
(Your MBJ would still require tye 12-1/2%)
 
Last edited:

housemoney

Member
Location
Midwest
Occupation
Engr
See Note 3 to the Table. For the grounded service conductor it depends on there being in one raceway or multiple raceways.
If you have (4) 500s in (4) separate raceways, each would have a 1/0 unless larger is required by load
(Your MBJ would still require tye 12-1/2%)

“required by the load” synonymous with what’s found in said table?
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
“required by the load” synonymous with what’s found in said table?
Not necessarily... There are some factors to consider: The neutral must be sized to carrry the calculated load per 220.61; it serves as the ground fault return path to the service supply so it must be sized per 250.102(C); and, when parallel conductors are involved, it can't be smaller than 1/0 per 310.10. You have to look all three of those requirements and determine the size required.
 