If all of your loads are wired line to line, but the service is a grounded wye, the neutral conductor must be brought to the service disconnect but need not be carried any further.I always thought that you had to have a grounded (neutral) conductor of the same size for 3 phase services. Am i wrong here?
yes there is a rule however there is also a rule that allows you to calculate the neutral load and then use a conductor sized accordingly. The only catch ist hat the grounded conductor must be sized at least as large as the gec. So I can have a 20amp service and have a #4 grounded conductor if that was sized for the load.I believe there is a rule for services 1200 amps and greater that allow the neutral to be smaller than the phase conductors.
I don't think so. In most cases, the grounded/grounding electrode/equipment grounding conductor is never required to be larger than ungrounded supply conductors.yes there is a rule however there is also a rule that allows you to calculate the neutral load and then use a conductor sized accordingly. The only catch ist hat the grounded conductor must be sized at least as large as the gec. So I can have a 20amp service and have a #4 grounded conductor if that was sized for the load.
yes there is a rule however there is also a rule that allows you to calculate the neutral load and then use a conductor sized accordingly. The only catch ist hat the grounded conductor must be sized at least as large as the gec. So I can have a 20amp service and have a #4 grounded conductor if that was sized for the load.
Also keep in mind that 100% of the load can be determined by 220.61...Service conductors(including the grounded conductor) are sized according to 230.42.
230.42(A)(1) says "The sum of the noncontinuous loads plus 125 percent of continuous loads"
The exception that follows says "Grounded conductors that are not connected to an overcurrent device shall be permitted to be sized at 100 percent of the continuous and noncontinuous load." So we typically only need to size the grounded conductor to 100 percent of load. The catch is there is a minimum size.....
230.42(C) says: "The grounded conductor shall not be smaller than the minimum size as required by 250.24(C)"