In one conduit I have;
2#8AWG (ckt. LPR-31/33) to CU2
2#10AWG (ckt. LPR-35/37) to ACU-2
2#8AWG (ckt. LPR-40/42) to CU-3
2#10AWG (ckt. LPR-36/38) to ACU-3
You skipped right over MCA MOCP and went right to derating...where is you soul?Eight current carrying conductors takes a 70% derating hit.
Has derating already been applied?
The 10s would only be rated 28 amps and the 8s only 38.5 amps.
You skipped right over MCA MOCP and went right to derating...where is you soul?
So many questions but MCA and MOCP are the reasons I did not state the max breaker size for those derated conductors.
Eight current carrying conductors takes a 70% derating hit.
Has derating already been applied?
The 10s would only be rated 28 amps and the 8s only 38.5 amps.
Both are 208 1ph.
According to Mechanical schedule the condenser units "CU-2 & CU-3" are MCA - 35A each, MOCP is 40A for each
AC units "ACU-2 & ACU-3" are MCA - 1A each, MOCP is 15A for each
The engineer used 40A breaker for each Condensor unit and 20A for each AC unit.
However the distance from each Condensor unit to panel is 192 FEET
Distance from each AC unit to panel is 155 Feet