A potential contractor raised a question about a design regarding sizing of grounding electrode conductors
Design in question consists of a 5000A service entrance main, with its neutral bus bonded to a building main ground bus via a #3/0 grounding electrode conductor, sized per table 250.66.
The main ground bus is to be bonded to:
-main water supply pipe via #3/0 (sized per table 250.66), and
-building rebar via #4 (max size required per 250.66(B)
-triad ground via #6 (see below)
My interpretation of 250.53(D)(2), is that using a water pipe as a grounding electrode, requires a supplemental electrode. This supplemental electrode can be the building structural metal (covered by bonding the rebar) or a ground rod. I believe this #6 is permitted as the maximum size per 250.53(E), and possibly 250.66(A).
The contractor is suggesting the triad needs to be tied together using #3/0 all the way to the building main bus bar to carry fault current. I contest that it is a waste of materials and labor, and isn't required by code, and isn't the intended or designed path of fault current which would be via the grounded conductor back to the utility.
I'm obviously biased by my own position, but I'd like some input, especially if my interpretations of the code are incorrect, or if I'm designing something that would be unsafe.
:thumbsup: or :thumbsdown:
-Jim
Design in question consists of a 5000A service entrance main, with its neutral bus bonded to a building main ground bus via a #3/0 grounding electrode conductor, sized per table 250.66.
The main ground bus is to be bonded to:
-main water supply pipe via #3/0 (sized per table 250.66), and
-building rebar via #4 (max size required per 250.66(B)
-triad ground via #6 (see below)
My interpretation of 250.53(D)(2), is that using a water pipe as a grounding electrode, requires a supplemental electrode. This supplemental electrode can be the building structural metal (covered by bonding the rebar) or a ground rod. I believe this #6 is permitted as the maximum size per 250.53(E), and possibly 250.66(A).
The contractor is suggesting the triad needs to be tied together using #3/0 all the way to the building main bus bar to carry fault current. I contest that it is a waste of materials and labor, and isn't required by code, and isn't the intended or designed path of fault current which would be via the grounded conductor back to the utility.
I'm obviously biased by my own position, but I'd like some input, especially if my interpretations of the code are incorrect, or if I'm designing something that would be unsafe.
:thumbsup: or :thumbsdown:
-Jim