I don’t know how I missed this after all these years. A 1200 amp service fed with 4 runs of 400 kcmil copper. A grounding electrode conductor to the underground water pipe is required to be 3/0 copper per 250.66. However, 250.104 requires a 4/0 copper for metal water piping ran throughout the building. (Table 250.102(C)(1) So, I would require a 4/0 copper grounding electrode conductor. Correct? This size would also include fire sprinkler pipe as well. Correct?