I don’t know how I missed this after all these years. A 1200 amp service fed with 4 runs of 400 kcmil copper. A grounding electrode conductor to the underground water pipe is required to be 3/0 copper per 250.66. However, 250.104 requires a 4/0 copper for metal water piping ran throughout the building. (Table 250.102(C)(1) So, I would require a 4/0 copper grounding electrode conductor. Correct? This size would also include fire sprinkler pipe as well. Correct?
 
First you define what the conductor actually is, a GEC is never required to be larger than #3/0. I do not see #4/0 copper in Table 250.102(C)(1) maybe you can elaborate.
 
Is the waterpipe an electrode? If so then I would think you could use 3/0... but that is interesting.. I don't know why they changed that table
 
Are you saying that you're using that table for bonding a water pipe that is not a grounding electrode? Is that connection a supply side bonding jumper? That table as stated in the notes is for:

*For the purposes of applying this table and its notes, the term bonding
jumper refers to main bonding jumpers, system bonding jumpers, and
supply-side bonding jumpers.
 
I don’t know how I missed this after all these years. A 1200 amp service fed with 4 runs of 400 kcmil copper. A grounding electrode conductor to the underground water pipe is required to be 3/0 copper per 250.66. However, 250.104 requires a 4/0 copper for metal water piping ran throughout the building. (Table 250.102(C)(1) So, I would require a 4/0 copper grounding electrode conductor. Correct? This size would also include fire sprinkler pipe as well. Correct?
The GEC only needs to be 3/0 CU as that is the max. for any GEC. The bonding jumper, as you know, does not max out. In your case the bonding jumper works out to 4/0 CU.
Take notice of 250.104(A)(1)(3). This recognizes that this happens.
 
I think the point is that 3/0 is sufficent as an electrode but the same water pipe not connected to the earth would need 4/0. The grounding electrode conductor does bond the water pipe when using it as an electrode but why the need for a larger size when it is bonded.
 
See 250.104(A)(1)(3)

This what that says

Grounding electrode conductor if of sufficient size--

But the grounding electrode conductor is not of sufficient size for a water pipe bond so are you saying 4/0 is needed? That is what I think
 
This what that says

Grounding electrode conductor if of sufficient size--

But the grounding electrode conductor is not of sufficient size for a water pipe bond so are you saying 4/0 is needed? That is what I think
Let's say that the water pipe electrode is isolated from the interior metallic piping. Then you could use a 3/0 to the pipe electrode but you would need a 4/0 to the interior piping.
 
It appears to say the grounding electrode conductor can be used as the bonding if it is of sufficient size. If the water pipe is an electrode and connected to the interior pipes wouldn't that require 4/0.
 