doug elias
Member
In an installation where parallel 3/0 conductors
have been installed to compensate for voltage drop, what code article dictates the size of the
grounding conductor? Are these conductors considered " Increased in size" per 250-122(B)
or are they considered "Conductors in Parallel"
per 250-122(F) The installation is for a 120/208 volt 225 amp 3 phase/4 wire panel located approx. 550' from the 200 amp disconnect that feeds it. this panel is fed by (2) sets of (4)
3/0 conductors in 3" pvc conduit
have been installed to compensate for voltage drop, what code article dictates the size of the
grounding conductor? Are these conductors considered " Increased in size" per 250-122(B)
or are they considered "Conductors in Parallel"
per 250-122(F) The installation is for a 120/208 volt 225 amp 3 phase/4 wire panel located approx. 550' from the 200 amp disconnect that feeds it. this panel is fed by (2) sets of (4)
3/0 conductors in 3" pvc conduit