Both state that the max OCP is 15A, so no, you can’t use a 20A breaker unless there is a 15A OCP device somewhere else.
Can’t comment on voltage drop with knowing the length of the branch circuit run.
 
Its a heater, running at 208V. Probably one of the least sensitive things to voltage drop there is. Nameplate load is around 7 amps. Unless the circuit is over 200' long, you are probably fine with #14. #12 on a 15A breaker could be run. Some industrial customers really don't like #14 and demand that all circuits be #12 or larger. But they need to be willing to pay for it.
 