blackbart10
Member
- Location
- N. CA
- Occupation
- agriculture production tech
I am installing a Yaskawa VFD to drive a 3ph 208/230V centrifugal pump. Power source is single phase 240V. The VFD is rated for 42A 3ph. 240V load. The actual load is 18.4A 230v 3ph per motor tag. According to the manufacture chart for using the VFD as a phase converter I need AWG #6 copper conducter protected by a 80 amp slow blow fuse or a 100amp cb for the derated load for the input lines.
If I take the 3ph. load amps x 1.732 I get approx. 32 amps single phase. Do I actually need to the 100A cb or does a 40A sufffice?
If I take the 3ph. load amps x 1.732 I get approx. 32 amps single phase. Do I actually need to the 100A cb or does a 40A sufffice?