Hey I’m back to make sure I haven’t overlooked anything or Mia calculated in my plans. Again any and all help is greatly appreciated.
I want to supply two separate structures from a wire way. Wireway will be supplied with 2 parallel runs of 3/0 copper. I’m planning on running 3/0 copper to each structure from the wire way.
Each structure will have a 200a service disconnect on the outside of the building.
All raceways will be pvc underground.
I will bond service disconnects using green screw provided from manufacturer.
I will run #4cu gec to water main and jump back outside to aground rod with #6 cu “if no water or other present electrodes I will set (2) ground rods and run #6cu
1st ? Would I be able to get the service disconnects inside?
Thought was lb from outside of each building right into the back of a panel inside or would that be a violation of 230.3 ?
2? Will my wireway need to be bonded?
If so looks like I would calculate using 250.102(c)(1)?
3/0cu=178.2x2=345.6mm2>350kcmil=1/0cu ssbj
3? Does my wireway need a gec as shown in exhibit 250.12 “see 2nd picture” or is this just another way to complete the grounding electrode system? If so I’m guessing it would be based in 250.66 which should be basically same formula above giving you 1/0cu
I want to supply two separate structures from a wire way. Wireway will be supplied with 2 parallel runs of 3/0 copper. I’m planning on running 3/0 copper to each structure from the wire way.
Each structure will have a 200a service disconnect on the outside of the building.
All raceways will be pvc underground.
I will bond service disconnects using green screw provided from manufacturer.
I will run #4cu gec to water main and jump back outside to aground rod with #6 cu “if no water or other present electrodes I will set (2) ground rods and run #6cu
1st ? Would I be able to get the service disconnects inside?
Thought was lb from outside of each building right into the back of a panel inside or would that be a violation of 230.3 ?
2? Will my wireway need to be bonded?
If so looks like I would calculate using 250.102(c)(1)?
3/0cu=178.2x2=345.6mm2>350kcmil=1/0cu ssbj
3? Does my wireway need a gec as shown in exhibit 250.12 “see 2nd picture” or is this just another way to complete the grounding electrode system? If so I’m guessing it would be based in 250.66 which should be basically same formula above giving you 1/0cu