Sizing Main Disconnect
girl
far away
Hello All,
Your help is appreciated!
Here is my question: The contractor installed 3 phase , 600 Volt disconnect at MCC. Disconnect has 3 fuses, 25 Amp each fuse, 600 volt.
It supplys power to a 100 Amp Panel.
On the panel there are some 15 Amp single pole breakers, three pole breakers for a water pump, some 40 Amp breakers, and or 20 Amp breakers.
My question is: is that 25 Amp Main Disconnect on MCC properly sized for this Panel?
Thank you everybody
I really hope that the person who made those selections was not counting on the three 25 amp fuses to supply a total of 75 amps. :happysad:
Your question cannot be answered (not enough information given), though an answer of "no" would be a really good bet. :happyyes:
The breaker ratings downstream of the three 25 amp fuses mean nothing. All that matters is the total calculated load. You might have a 40 amp breaker serving a load that actually draws only a couple amps. But it is more likely that the total amount of load that all those breakers serve would exceed 25 amps, and that will be a problem.
Is there a transformer involved?
gotta be.... i've never seen a 480 volt 100 amp panel.
does anyone even make something like that?
and 1 pole 15 amp 480 volt breakers.....
sounds like someone fed a transformer out of a 30 amp bucket
in a MCC...... to a 100 amp panel.... so that would give you
roughly 50 amps at the panel.... it'll probably work if you don't
turn everything on at once.... :p
25 amp primary fuses would work for the primary protection of a 15KVA, 480-120/208V transformer. Putting a 100 amp 120/208V panel downstream of that transformer would also work. But it would need to have a main circuit breaker rated at 50 amps or less, or it would need a similarly rated overcurrent device upstream of the 100 amp panel. You didn't mention whether the 100 amp panel had a main breaker.
As I said at first, the question did not give us enough information to allow us to provide a useful answer. Can you tell us more?