Sizing MBJ and its material

Status
Not open for further replies.

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
I have incoming service conductors of 3 sets of 500kcmil AL.

So to size MBJ I have 3x500=1500 kcmil. 1500x0.125=187.5kmil which is 4/0.

1. So then that 4/0 is it AL or Copper? Which material?
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
The way I read the Table you could elect to use a 2/0 Cu MBJ.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
What are you using for service equipment? All equipment that is listed as "suitable for use as service equipment" has a factory supplied MBJ. You simply install the factory provided part and forget about any calculations.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Didnt want to start another thread but what would the MBJ be in copper for service conductors of 3 sets of 500kcmil AL?
Look below:

Table 250.102(C)(1) Grounded Conductor, Main Bonding Jumper, System Bonding Jumper, and Supply-Side Bonding Jumper for Alternating Current Systems
 

qcroanoke

Sometimes I don't know if I'm the boxer or the bag
Location
Roanoke, VA.
Occupation
Sorta retired........
What are you using for service equipment? All equipment that is listed as "suitable for use as service equipment" has a factory supplied MBJ. You simply install the factory provided part and forget about any calculations.
So are you saying the bonding screw can act as the main bonding jumper?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
So are you saying the bonding screw can act as the main bonding jumper?
Don is asking if this is service equipment which typically has a factory supplied MBJ (screw, strap, bus bar). If so then why the question on how to size a wire type MBJ?
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
So are you saying the bonding screw can act as the main bonding jumper?
Yes, the factory supplied screw is the main bonding jumper for equipment that is listed as "suitable for use as service equipment". The listing standard requires that the manufacture provide a main bonding jumper suitable for the rating of the service equipment. For the application in this thread it would not be a screw, but as bus connection or bus bar.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Don is asking if this is service equipment which typically has a factory supplied MBJ (screw, strap, bus bar). If so then why the question on how to size a wire type MBJ?
Because the title of the thread is "Sizing MBJ and its material". I have no idea what he is really asking about. If you are connecting to listed service equipment, the manufacture is required to provide the main bonding jumper.
 

Canton

Senior Member
Location
Virginia
Occupation
Electrician
Because the title of the thread is "Sizing MBJ and its material". I have no idea what he is really asking about. If you are connecting to listed service equipment, the manufacture is required to provide the main bonding jumper.
It’s possible it was lost/misplaced on the job. I had to make a few MBJ in the past
 