Hi All,
I have some questions about sizing a Panelboard MCB based upon the total connected kVA load. Panelboard is a 208/120v, 3Phase.
If I have a Panelboard with a total connected load of 78.3 kVA: 78300/208√3 = 217 Amps. How would you size this panelboard?
- Connected load amps (217 A) and add a 10% or 25% spare capacity margin?
- Size based on next C/B size up from 217 -> 225A MCB?
- Add a Spare Capacity margin and then go to the next C/B size up? 217 * 1.25 (25% Spare Capacity) = 272 Amps -> 300 Amp MCB?
- Should you ever size a Panelboard MCB based off of the 80% circuit breaker load rule?
If there are any more tips about sizing MCBs for Panelboards, it is greatly appreciated. I'm a younger design engineer trying to build good design practices.
Thanks in advance!