Good evening
We are installing 20 HP roller feed mill. We have GE 6000 series MCC with spare bucket with MCP and starter sized for 3 HP blower which is not used. I would like to retofit the bucket for 20 HP motor...FLA 27 at 460 V. I know I will need NEMA Size 2 starter with thermal O/L relay. DO not desire electronic O/L relay. I think the MCP I need is GE TEC36030. This this MCP is rated for 30 amp continuious and adj. mag trip of 90-360 amp. Am I correct?
We are installing 20 HP roller feed mill. We have GE 6000 series MCC with spare bucket with MCP and starter sized for 3 HP blower which is not used. I would like to retofit the bucket for 20 HP motor...FLA 27 at 460 V. I know I will need NEMA Size 2 starter with thermal O/L relay. DO not desire electronic O/L relay. I think the MCP I need is GE TEC36030. This this MCP is rated for 30 amp continuious and adj. mag trip of 90-360 amp. Am I correct?