I did not search this site, sorry if this has been discussed.
430.245 states to follow Part VI of Article 250 for method of grounding.
In Part VI or Article 250:
250.122(D)(1) General. The equipment grounding conductor size shall not be smaller than determined by 250.122(A) based on the rating of the branch-circuit short-circuit and ground fault protective device.
If one was to install a protective device as per 430.52(C)(1) Exception 2 for instance. Say a 100A rated motor using a nontime-delay fuse (which would permit the overcurrent protective device to 400%), would one not be required to upsize the the EGC (copper)? From an 8Awg to a 3 Awg
Thanks for the help!