This is my first post of many im sure. Its great having a forum full of fellow electricians and people of related fields. So heres the issue
MY boss and I were sizing out the Branch-circuit Short-circuit and Ground-fault protective device (which i will from now on abbreviate BC SC & GFP). WE have several 1hp 240v fan motors. I ran into "430.53 Several Motors or Loads on One Branch-Circuit". 430.53B states, verbatim:
If the bc sc &gfp device is selected not to exceed that allowed by 430.52 for the smallest rated motor, two or more motors or one or more motors and other loads, with each having individual overload protection, shall be permitted to be connected to a branch circuit where it can be determined that the bc sc & gfp device will not open under the most severe normal conditions of service that might be encountered.
There is no need to get into the math as i understand that. My problem is it says you cant exceed the rating of the bc sc & gfp device of the smallest motor sized according to 430.52 Not table 430.52 just 430.52.
WE are going to use an inverse time breaker. Which is 250% of your FLC according to Table 430.52. That number allows us to have two motors on one 20 amp breaker, assuming it can handle the inrush of two motors starting at once. BUt there is an exception to table 430.52 which states the rating of an inverse time breaker can increase to but not exceed 400% of the FLC. Using that excepiton we could fit one more motor on a single circuit (assuming ofcoarse that the breaker could handle the inrush of all the motors starting). Could we use that exception based on how 430.53B is worded? And i mean in general not just for my specific instance.
Thanks in advance for your replies
This is my first post of many im sure. Its great having a forum full of fellow electricians and people of related fields. So heres the issue
MY boss and I were sizing out the Branch-circuit Short-circuit and Ground-fault protective device (which i will from now on abbreviate BC SC & GFP). WE have several 1hp 240v fan motors. I ran into "430.53 Several Motors or Loads on One Branch-Circuit". 430.53B states, verbatim:
If the bc sc &gfp device is selected not to exceed that allowed by 430.52 for the smallest rated motor, two or more motors or one or more motors and other loads, with each having individual overload protection, shall be permitted to be connected to a branch circuit where it can be determined that the bc sc & gfp device will not open under the most severe normal conditions of service that might be encountered.
There is no need to get into the math as i understand that. My problem is it says you cant exceed the rating of the bc sc & gfp device of the smallest motor sized according to 430.52 Not table 430.52 just 430.52.
WE are going to use an inverse time breaker. Which is 250% of your FLC according to Table 430.52. That number allows us to have two motors on one 20 amp breaker, assuming it can handle the inrush of two motors starting at once. BUt there is an exception to table 430.52 which states the rating of an inverse time breaker can increase to but not exceed 400% of the FLC. Using that excepiton we could fit one more motor on a single circuit (assuming ofcoarse that the breaker could handle the inrush of all the motors starting). Could we use that exception based on how 430.53B is worded? And i mean in general not just for my specific instance.
Thanks in advance for your replies