Please see below:
1. Per NEC 2017, Table 310.60(C)(79), One Circuit, 5001-35,000 volts, a single 500 kcmil has an ampacity of 450 A at 90 deg C and 485 A at 105 deg C.
2. For Two Circuits, in parallel, the aforementioned ampacities have to be multiplied by 0.88 (NEC 2017, Informative Annex B, B.5(a). So, the reduced ampacities are 396 A at 90 deg C and 426.8 A at 105 deg C
3. The load of the four (4) unit substations at 13.2 kV is 210 Amps (4800 kVA/(SQRT(3)x13.2kV) x 4 = 840 Amps.
4. We can’t specify two (2) conductors per phase, in 5” PVC duct (which is only rated for 90 deg C), as they just fall short (2 x 396 A = 792 A). Therefore, our recommendation is to use 5” RTRC (aka fiberglass duct), which will allow operating the 500 kcmil at the higher temperature of 105 deg C and ampacity of 426.8 A (2 x 426.8 A = 853.6 A).
Nick is the clients electrical engineer. I am the designing consultant.
The unit substations for the Paint shops have 5,000A M-T-M circuit breakers on the 480V bus.
Nick’s contention is that I should have used the HV amperes equivalent to the 5,000 A, i.e. 181.82 amps, to size the MV cable. This would then allow the use of the 5” PVC duct.
Your thoughts?
1. Per NEC 2017, Table 310.60(C)(79), One Circuit, 5001-35,000 volts, a single 500 kcmil has an ampacity of 450 A at 90 deg C and 485 A at 105 deg C.
2. For Two Circuits, in parallel, the aforementioned ampacities have to be multiplied by 0.88 (NEC 2017, Informative Annex B, B.5(a). So, the reduced ampacities are 396 A at 90 deg C and 426.8 A at 105 deg C
3. The load of the four (4) unit substations at 13.2 kV is 210 Amps (4800 kVA/(SQRT(3)x13.2kV) x 4 = 840 Amps.
4. We can’t specify two (2) conductors per phase, in 5” PVC duct (which is only rated for 90 deg C), as they just fall short (2 x 396 A = 792 A). Therefore, our recommendation is to use 5” RTRC (aka fiberglass duct), which will allow operating the 500 kcmil at the higher temperature of 105 deg C and ampacity of 426.8 A (2 x 426.8 A = 853.6 A).
Nick is the clients electrical engineer. I am the designing consultant.
The unit substations for the Paint shops have 5,000A M-T-M circuit breakers on the 480V bus.
Nick’s contention is that I should have used the HV amperes equivalent to the 5,000 A, i.e. 181.82 amps, to size the MV cable. This would then allow the use of the 5” PVC duct.
Your thoughts?